Change Function Display name of I/O in MPC20

Post by [rahul 9219] » Sun Dec 10, 2017 11:35 pm

Hi Everyone,

I want to change the display name of the function of the digital input (snapshot below in attachment):

Like under function "User1, User2, ... User6" is available i want to give customized name and corresponding will have warning/shutdown, so Error message should also be edited as according.

Please suggest the steps for this.
I had gone through the Advanced Mode of controller and tried, but Display name is highlighted, not able to click for change. Rather I am able to change the function display name of the other section.

Is it being protected by the Password something like that. Please Support.
Attachments
Change Function Display name of IO in MPC20 =forum.fwmurphy.jpg
Change Function Display name of IO in MPC20 =forum.fwmurphy.jpg (120.63 KiB) Viewed 56 times
-Thanks
Rahul J. G.
boyce
Enovation Controls Development
Enovation Controls Development
Posts: 322
Joined: Wed Sep 08, 2010 5:09 pm

Re: Change Function Display name of I/O in MPC20

Post by boyce » Mon Dec 11, 2017 10:42 am

The User defined strings for the Input Function and the Alert can be changed in the Languages section.
mpc20-1.JPG
mpc20-1.JPG (164.54 KiB) Viewed 48 times
mpc20-2.JPG
mpc20-2.JPG (359.15 KiB) Viewed 48 times
The same strings show up in the Global Lockout Bubble Parameters. I didn't see it anywhere else.