Hi,
how can the PV380r2 got back to boot mode for reprogramming? My PV380 is actually stop receiving CAN-messages and no more reachable by the ECOM adapter. This is maybe caused by a programming error of myself (trying to send CAN-messages via Free Form Numeric Message). Only one time I reached the PV380 by pressing buttons during power up the device (that I know from the PV780 with USB-stick connected), but this procedure isn't working as expected.
Is there any hint (pressing buttons during startup)?
broesch
Posts: 10
Joined: Thu Jun 02, 2016 5:07 am

Re: PV380 reboot connection

Post by broesch » Tue Dec 12, 2017 9:00 am

Hi again,

I got the PV380 running again:
Boot.JPG
Boot.JPG (44.17 KiB) Viewed 103 times
The trick is to load (click on "load all" button) the Application Install Package (any created which was working) during power on of the display!
I'm wondering, if this is not described in the documentation, I didn't found any hint?
boyce
Enovation Controls Development
Enovation Controls Development
Posts: 322
Joined: Wed Sep 08, 2010 5:09 pm

Re: PV380 reboot connection

Post by boyce » Tue Dec 12, 2017 3:48 pm

Maybe you got lucky! I believe you hold down the first and last button (far left and far right) while powering on.
Boyce Schrack
Enovation Controls
broesch
Posts: 10
Joined: Thu Jun 02, 2016 5:07 am

Re: PV380 reboot connection

Post by broesch » Wed Dec 13, 2017 12:44 am

Hi Boyce,

true, but this wasn't really done directed by myself, because I tried nearly everything to get the display running.
Is there any official way to regear the control of the display in such case?
boyce
Enovation Controls Development
Enovation Controls Development
Posts: 322
Joined: Wed Sep 08, 2010 5:09 pm

Re: PV380 reboot connection

Post by boyce » Wed Dec 13, 2017 8:32 am

Power on the display while holding the first and last buttons to stop the display in the bootloader. Then load a full install file with PowerVision or the Toolkit.
Boyce Schrack
Enovation Controls
broesch
Posts: 10
Joined: Thu Jun 02, 2016 5:07 am

Re: PV380 reboot connection

Post by broesch » Wed Dec 13, 2017 8:37 am

Hi Boyce,

many thanks, I'll try it next time, when loosing connection!