PV750/J1939 Termination Resistor

Discuss issues and ideas you have to configuring displays with PowerVision
tshiii
Posts: 79
Joined: Thu Sep 09, 2010 8:56 pm

PV750/J1939 Termination Resistor

Post by tshiii » Fri Sep 13, 2013 3:55 am

Dear Sir,

Regarding the subject, J1939 Termination Resistor can be checked or unchecked in System Settings. Please find attached. Please let me know how this function is.

Best regards,
Shiii
Attachments
RIMG1048.JPG
RIMG1048.JPG (94.22 KiB) Viewed 99 times
pcebuhar
Enovation Controls Development
Enovation Controls Development
Posts: 23
Joined: Tue Feb 07, 2012 4:08 pm

Re: PV750/J1939 Termination Resistor

Post by pcebuhar » Mon Sep 16, 2013 12:47 pm

Dear Shiii-san,
On high speed serial communication channels (such as Video channels or Mil-STD-1553 or the CAN Bus where you have multiple devices connected) you typically need to terminate the bus to prevent ringing or reflection of the signal on the bus. The CAN bus is no different and it needs a 120 ohm resistor in parallel (between the High and Low signal lines) at typically the last device on the bus. Most devices, such as Engine Control Units, do not provide the termination or it may be incorporated in the cable or better yet the termination is provided in the software configuration of the display.

It has been our experience that absolutely no termination is very bad for communication. You will see missed and corrupted messages. If you have some other device which is terminated, communication should be good. If you have extra devices provide termination, the communication should continue to be good. If your are not sure about whether the bus is terminated or not, set the Display configuration to include termination even if you have multiple displays running the same Configuration file. We have not seen an issue with too much termination.
Thanks,
Phil Cebuhar
tshiii
Posts: 79
Joined: Thu Sep 09, 2010 8:56 pm

Re: PV750/J1939 Termination Resistor

Post by tshiii » Wed Sep 18, 2013 7:53 pm

Dear Phil-san,

Thank you for your attention and explanation.

If I check the box of "Enable CAN1" on the system settings, termination is provided and no other termination resistors do not need to be added in the CANbus line. Is my understanding correct? Before and after I checked the "Enable CAN1", I measured actual resistance values in the CANbus line connected with the PV750, but there was any difference between the measured values.

Best regards,
Shiii
jbilleter
Posts: 87
Joined: Fri Oct 15, 2010 6:49 pm

Re: PV750/J1939 Termination Resistor

Post by jbilleter » Thu Sep 26, 2013 12:47 pm

Dear Shiii,

I believe a power cycle is required when enabling/disabling the terminating resistor via software. Try a power cycle and then measure across the CAN high and low terminals.

-Jacob
Jacob Billeter
Staff Engineer - MurCal, Inc.