I have PV750 w/ Bootloader 2.2.10010 on it.
I seem to remember that this should be compatible with Power Vision 2.3 but cannot get my PV750 to communicate with the 2.3 software. It works fine with the 2.2 software.
Is 2.2 the current bootloader version? Is it compatible with the 2.3 software? If not, where can I get the updated bootloader?
Current Bootloader version?
- natem
- Posts: 5
- Joined: Tue Apr 26, 2011 10:00 am
- bmcrae
- Enovation Controls Development
- Posts: 75
- Joined: Thu Sep 09, 2010 11:20 am
Re: Current Bootloader version?
natem,
The bootloader you listed is compatible with 2.3. You will have to make a Full install from the tool, at least for the first load into the unit. Can you describe in more detail the errors you are seeing?
Brian McRae
SW Test
FW Murphy
The bootloader you listed is compatible with 2.3. You will have to make a Full install from the tool, at least for the first load into the unit. Can you describe in more detail the errors you are seeing?
Brian McRae
SW Test
FW Murphy
- natem
- Posts: 5
- Joined: Tue Apr 26, 2011 10:00 am
Re: Current Bootloader version?
Well I downloaded the 2.3 Demo Config from here:
viewtopic.php?f=26&t=505
I loaded it into Power Vision 2.3.11147. I then created a full install package and put it on my thumb drive and tried loading it onto the PV750. It finds the config and attempts to load it but I get this error:
Invalid configuration version: 2311147
Application version: 2.2.10022.0
Required configuration tool version: 2.2.10320 to 2.2.19999
viewtopic.php?f=26&t=505
I loaded it into Power Vision 2.3.11147. I then created a full install package and put it on my thumb drive and tried loading it onto the PV750. It finds the config and attempts to load it but I get this error:
Invalid configuration version: 2311147
Application version: 2.2.10022.0
Required configuration tool version: 2.2.10320 to 2.2.19999
- natem
- Posts: 5
- Joined: Tue Apr 26, 2011 10:00 am
Re: Current Bootloader version?
Never mind.
I forgot to create a full install as opposed to creating a regular config install. Does that mean I need to create a full install for any configuration created in Power Vision 2.3? Or is it only the first time I load a 2.3 config?
Thanks for the help!
I forgot to create a full install as opposed to creating a regular config install. Does that mean I need to create a full install for any configuration created in Power Vision 2.3? Or is it only the first time I load a 2.3 config?
Thanks for the help!
- ECS-SA
- Posts: 48
- Joined: Thu Feb 17, 2011 7:19 am
Re: Current Bootloader version?
Hi,
It will only be for the first time you load a 2.2 screen with 2.3 from there on you can just make normal installs and also use direct connection to the display.
It will only be for the first time you load a 2.2 screen with 2.3 from there on you can just make normal installs and also use direct connection to the display.