HI All
I use TSC1 to control engine speed in ML2000.
I want to remote to control engine speed by digital input in auto mode, 800RPM to sent engine when digital4 is closed, 1500RPM is sent engine when digital5 is closed, but can't achieve, How to implement?
dwills
Enovation Controls Development
Enovation Controls Development
Posts: 26
Joined: Fri Jul 30, 2010 8:27 am

Re: MPC20

Post by dwills » Wed Aug 20, 2014 1:05 pm

The speed inputs only work in manual mode.

If you have the full configuration tool, you should be able to modify the Set Enine PID Setpoint activity by removing the check for manual mode. This configuration would only be valid if the throttle method is set to maximum RPM. The controller will not be able to control to a level, pressure or flow with this type of throttle.

The throttle type must be set to TSC1 and the digital inputs need to be set to speed inputs and the speed setpoints set accordingly.

No changes are neccessary to the configuration to use the digital inputs in manual mode.