PV 350 Digital
How do I turn on the digital output on PV 350 to fire on warning or shutdown. Using 2.7
- stalley
- Enovation Controls Development
- Posts: 618
- Joined: Tue Mar 18, 2014 12:57 pm
Re: PV 350 Digital
Hello dblye,
The recommended way is to enable the Digital Output on the Connections tab. You can auto create a variable when the output is enabled or you can select a variable you have created in the Programming tab.
Setting the variable to 1 will turn "ON" the digital output (close to ground)
Setting the variable to 0 will turn "OFF" the digital output (open)
The recommended way is to enable the Digital Output on the Connections tab. You can auto create a variable when the output is enabled or you can select a variable you have created in the Programming tab.
Setting the variable to 1 will turn "ON" the digital output (close to ground)
Setting the variable to 0 will turn "OFF" the digital output (open)