Dear All
I am working on a project which requires communication between MeCAN and PV101 C.
Basically i want to display engine oil pressure, coolant temperature and engine speed on PV101 C using sensors.
Please advice.
Regards
Zakir Sayed
Project Engineer
Rajkot Marine LLC
Ajman Jerf. U.A.E
MeCAN and PV101 C
- zakirrajkot
- Posts: 6
- Joined: Wed May 29, 2013 11:22 pm
- key
- Posts: 1
- Joined: Wed Jun 26, 2013 3:28 am
Re: MeCAN and PV101 C
I also want to know about it! LOL
- zakirrajkot
- Posts: 6
- Joined: Wed May 29, 2013 11:22 pm
Re: MeCAN and PV101 C
Hi Key
Finally I got a solution for this..
MeCAN and PV101C can serve this purpose.
Actually its very simple..
1.You need to confirm correct wiring of CAN wires between two device
2.Position OF DIP switches should be as per manual.
Once communication is established MeCAN LED will be steady ON .
With Best Regards
Zakir Sayed
Finally I got a solution for this..
MeCAN and PV101C can serve this purpose.
Actually its very simple..
1.You need to confirm correct wiring of CAN wires between two device
2.Position OF DIP switches should be as per manual.
Once communication is established MeCAN LED will be steady ON .
With Best Regards
Zakir Sayed
- Attachments
-
- Murphy MeCAN.PDF
- MeCAN Installation and Operational Manual
- (207.3 KiB) Downloaded 16 times