Discuss issues and ideas you have to configuring displays with PowerVision
akhilpauly
Posts: 16
Joined: Fri Mar 14, 2014 8:02 am

PV 350 communication with Power vision tool

Post by akhilpauly » Wed Nov 26, 2014 8:35 am

Dear Sir,
We connected the PV 350 display to power vision configuration tool 2.7.10419, but we could not able to make communication with PV 350 device and PV config. tool. So please advise the steps of communication procedure...
Akhil Pauly Abraham
Tech. Sales & Service Engineer
Rajkot Marine LLC- UAE

rajkotsales2012@gmail.com
stalley
Enovation Controls Development
Enovation Controls Development
Posts: 618
Joined: Tue Mar 18, 2014 12:57 pm

Re: PV 350 communication with Power vision tool

Post by stalley » Wed Dec 03, 2014 5:47 pm

Hello,

I apologize that I didn't see your post sooner.

Have you been able to resolve this problem? If not, I would recommend contacting our technical services department, http://www.fwmurphy.com/resources-suppo ... al-support. This link provides a phone number or you can fill out a form to request technical support.

The latest PowerVision Configuration Studio manuals are found here viewtopic.php?f=3&t=932. The Powervision Configuration Studio Core manual has some information about communicating between PowerVision Configuration Studio and a display along with some troubleshooting.

Since your display is a PV350, it will use CAN. Be sure to have the 120 ohm resistor on the connection.

Again, I apologize that I didn't see your post sooner.
Sara Talley
Software Engineer
Enovation Controls