Hello,
I got an application the hardware setup by 3 controllers and PV450.
Now, the controller manufacuturer customize some CAN datas. They used a SPN to define two different variables with different Source Address coming from different controllers.
These Variables are programmed to display is not a problem, but how to handle the DTCs of these variables?
I can add some DTCs under the DTC tab of Database, input SPN & FMI , select Light Override and enter Message, then hit Save button, and there is a event log says: More that one DTC exists with the same SPN FMI code.....
How do I handle these? Also if two engines are connected with 1 PV450/750, how to display the same SPN & FMI just like :
SPN 110 FMI 16 Engine #1 coolant temperature is high
SPN 110 FMI 16 Engine #2 coolant temperature is high
Thanks.
Terry
PV450 DTCs
- twang
- ksaenz
- Enovation Controls Development
- Posts: 263
- Joined: Thu Aug 19, 2010 7:53 am
Re: PV450 DTCs
Hello Terry,
You can only have one message per SPN, FMI combination.
To know if the DTC is coming from engine 1 or engine 2 you can display the variable "UserDefinedVariable.Dm1.SourceAddress" with a text gauge or "UserDefinedVariable.Dm1.DeviceNameId" with an indirect text widget like the Murphy Standard Configuration.
Regards,
ksaenz
You can only have one message per SPN, FMI combination.
To know if the DTC is coming from engine 1 or engine 2 you can display the variable "UserDefinedVariable.Dm1.SourceAddress" with a text gauge or "UserDefinedVariable.Dm1.DeviceNameId" with an indirect text widget like the Murphy Standard Configuration.
Regards,
ksaenz