Dm1.SPN Variable Stuffing

Post by dmsellers » Tue Nov 12, 2013 4:41 pm

Hello,

Display - PV350
Configuration Studio 2.6.20023

I have mapped a DTC message from a non-engine controller with an SPN=3171d and FMI=15d. If a DM1 message is sent from the controller with a 3171d/15d fault AND the CM bit is "0", the PV350 Dm1.SPN variable contains 3171d and Dm1.FMI variable contains 15d as expected. If the CM bit is "1", the PV350 Dm1.SPN variable contains 65535d and the Dm1.SPN variable still contains the expected 15d. As is happens, the controller that is sending me the DM1 messages uses the older DM1 format (J1939-73 rev. SEP2006 Section 5.7.1.11 version 3) where the CM bit is set to a "1" but still follows the expected byte/bit mapping of a typical (specified) DM1 message. Am I missing something?

Thanks,

Dan
ksaenz
Enovation Controls Development
Enovation Controls Development
Posts: 263
Joined: Thu Aug 19, 2010 7:53 am

Re: Dm1.SPN Variable Stuffing

Post by ksaenz » Wed Nov 13, 2013 11:34 am

Hello Dan,

Looks like you need to adjust the variable "Dtc.FaultConversion" where:
0 = Version 1
1 = Version 2
2 = Version 3

Regards,
ksaenz
dmsellers
Posts: 42
Joined: Mon Aug 12, 2013 7:45 pm

Re: Dm1.SPN Variable Stuffing Incorrect Value?

Post by dmsellers » Thu Nov 14, 2013 10:48 pm

Has anybody come across this issue? Right now, it seems my only solution is to abandon the built-in Dm1 handler and write custom code to parse out all 400+ Dm1 messages from the controller.

Any help appreciated.

Dan
dmsellers wrote:Hello,

Display - PV350
Configuration Studio 2.6.20023

I have mapped a DTC message from a non-engine controller with an SPN=3171d and FMI=15d. If a DM1 message is sent from the controller with a 3171d/15d fault AND the CM bit is "0", the PV350 Dm1.SPN variable contains 3171d and Dm1.FMI variable contains 15d as expected. If the CM bit is "1", the PV350 Dm1.SPN variable contains 65535d and the Dm1.SPN variable still contains the expected 15d. As is happens, the controller that is sending me the DM1 messages uses the older DM1 format (J1939-73 rev. SEP2006 Section 5.7.1.11 version 3) where the CM bit is set to a "1" but still follows the expected byte/bit mapping of a typical (specified) DM1 message. Am I missing something?

Thanks,

Dan
Dan Sellers
DCS Technologies
http://www.dcstechinc.com
dmsellers
Posts: 42
Joined: Mon Aug 12, 2013 7:45 pm

Re: Dm1.SPN Variable Stuffing

Post by dmsellers » Fri Nov 15, 2013 9:07 am

Thanks ksaenz for pointing me in the right direction. Setting the conversion variable to the proper initial value did the trick. Just so I understand the documentation and/or functionality, in document 00-02-0873 Apps Ref Manual, the Diagnostic Messages Variable Description Table describes the Dtc.FaultConversion variable as being Populated by the DM App as opposed to the Developer. Does that mean the DM App can overwrite the initial value?

Thanks,

Dan
ksaenz wrote:Hello Dan,

Looks like you need to adjust the variable "Dtc.FaultConversion" where:
0 = Version 1
1 = Version 2
2 = Version 3

Regards,
ksaenz
Dan Sellers
DCS Technologies
http://www.dcstechinc.com
ksaenz
Enovation Controls Development
Enovation Controls Development
Posts: 263
Joined: Thu Aug 19, 2010 7:53 am

Re: Dm1.SPN Variable Stuffing

Post by ksaenz » Mon Nov 18, 2013 7:56 am

I see that and that is a mistake. The app will not overwrite the variable.

Regards,
ksaenz
dmsellers
Posts: 42
Joined: Mon Aug 12, 2013 7:45 pm

Re: Dm1.SPN Variable Stuffing

Post by dmsellers » Mon Nov 18, 2013 8:04 am

Thanks

Dan
Dan Sellers
DCS Technologies
http://www.dcstechinc.com